    GFCI Question

    GFCI Question

    I have a Hot Springs Spa. There is 110 v at the outlet. The power cord from the spa terminates in a large plug which contains a GFCI. The plug is a proprietary Hot Spring Spa unit with the GFCI built into it. Therefore, I cannot change it like could change a GFCI in a house outlet.

    The spa is dead. That’s as dead as if it were in the middle of the Sahara desert 100 miles from the nearest source of power (no lights, no motor, no heat, no etc.).

    GFCI

    The GFCI pilot light is on so there is power getting to the unit.
    Press the “Reset” button and the pilot light goes off.
    Release the “Reset” button and the light comes back on.

    Press the “Test” button and the light goes out.
    Press the “Reset” button and the light comes back on. I pressed the “Reset” button immediately after the “Test” button and I repeated the procedure again with a couple minutes before pressing the “Reset” button. The results were the same.

    When pressing the “Test” or “Reset” button there is a “click” sound. However, there is only a slight movement of the “Reset” button, not a large movement like the GFCI button on the outlets in the house.

    In all instances the spa just sat there doing nothing.

    The problem could be elsewhere. However, it really appears that power is just not getting to the spa. If the problem was an overheating motor tripping its own “Reset” button, it would not kill the entire spa. I could not find a “Reset” button on the heating unit.

    Any and all advice will gratefully be accepted and I thank you in advance.

    Enjoy,

    Jim
    First of all you have to be smarter than the machine.
    VOTING MEMBER

  2. #2
    Join Date
    Dec 2006
    Location
    RETIRED(!) in Austintown, Ohio
    Posts
    5,319
    If the spa is still under warranty, then let Hot Springs take care of it.

    If it's beyond warranty, then - using a meter - check for voltage at the power panel inside the spa. If there's power there, then it ain't the GFCI.

    If it IS the GFCI, then I'd be likely to cut it off, replace it with a regular plug, and MOST IMPORTANTLY(!), replace the outlet it's plugged into with a GFCI outlet.

    But that's just me. You might want to buy a new power cord, with GFCI, from Hot Springs, and install it yourself.
    Jim D.
    Adapt, Improvise, Overcome!

  3. #3
    Join Date
    Feb 2007
    Location
    Catalunya
    Posts
    4,632
    Maybe there is a safety fuse inside that's blown, and that only prevents the pump work
    Best regards,
    Toni

    __________________________________________________ __________________________________________________ _________________
    web site:http://www.toniciuraneta.com
    I also dream of a shop with north light where my hands can be busy, my soul rest and my mind wander...

  4. #4
    Join Date
    Jun 2008
    Location
    GTA Ontario Canada
    Posts
    12,247
    I would follow Jims advice to the letter. You might want to check the rating on the motor though to make sure the GFCI receptacle you put in place can handle that current. That would apply to the breaker feeding the GFCI circuit in your main panel.

    Question is why was the motor tripping in the first place. I presume the motor is driving a pump or sorts. Is the pump fine not seized. If the hottube is empty ie dry pump see if the motor shaft can be rotated reasonably freely. Maybe something got in the pump and jammed or is wedging the pump loading the motor beyond spec and causing the motor trip.
    cheers

  5. #5
    Join Date
    Mar 2008
    Location
    NH
    Posts
    4,005
    Just went through that with the pool. On mine the gfi outlet was bad
    It could be worse You could be on fire.
    Stupid hurts.

  6. #6
    Join Date
    Jun 2007
    Location
    Oceanside, So. Calif. 5 mi. to the ocean
    Posts
    4,944
    Hi,

    Like I say, "Don't get old, your brains leak out." I can't believe I was so dumb---I didn't check the voltage on the other end of the line. I will do so first thing in the morning---well not first thing, I'll let it warm up a little.

    Thanks and Enjoy,

    Jim
    First of all you have to be smarter than the machine.
    VOTING MEMBER

  7. #7
    Join Date
    Nov 2006
    Location
    Delton, Michigan
    Posts
    17,470
    call glenn he would be glad to fix it for you this wknd he hasnt anything else going on
    If in Doubt, Build it Stout!
    One hand washes the other!
    Don't put off today till tomorrow!

  8. #8
    Join Date
    Jun 2008
    Location
    GTA Ontario Canada
    Posts
    12,247
    Larry I dont think Glenn is posting here anymore with hints like that flying left right and center. He is in hiding in another state until Jim gets the hot tub fixed.
    cheers

  9. #9
    Join Date
    Nov 2006
    Location
    Delton, Michigan
    Posts
    17,470
    hey has anyone seen glenn arond his dad is need of some electrical help so he can have his bath water warmed up calling sonny come help out the old fellar
    If in Doubt, Build it Stout!
    One hand washes the other!
    Don't put off today till tomorrow!

  10. #10
    Join Date
    Oct 2006
    Location
    somewhere east of Queen Creek, AZ - South East of Phoenix
    Posts
    8,529
    Quote Originally Posted by larry merlau View Post
    hey has anyone seen glenn arond his dad is need of some electrical help so he can have his bath water warmed up calling sonny come help out the old fellar
    He said something about going up to antioc for the 4th. Thats near San Francisco.
    "There’s a lot of work being done today that doesn’t have any soul in it. The technique may be the utmost perfection, yet it is lifeless. It doesn’t have a soul. I hope my furniture has a soul to it." - Sam Maloof
    The Pessimist complains about the wind; The Optimist expects it to change;The Realist adjusts the sails.~ William Arthur Ward