    Question 200 Amp service on 2 AWG WIRE?

    Well, finally got the permanent service turned on at the house and when they came out to run a new wire to the house they did two things that had me worried. First, they tapped into a line that feed a house next door. Then they only use 2 Awg alum wire. This seems to be way to small to run one 200 amp service let alone two houses. I am just nervous about hooking up any of the machine to the service and causing problem with the motors not pulling enough power. By the way everything in the house is electric. What should I do?

  2. #2
    Join Date
    Mar 2010
    Location
    Decatur, Alabama
    Posts
    518
    Who hooked up the wiring, the local utility or a private contractor? I'd get in touch with the building department or utility company. I'm no electrician, but everything I've seen 2 wire isn't even good enough for 100 amp service to code or mfg.

  3. #3
    The current rating of wire increases in free air.
    Bob
    Making saw dust in SW Louisiana

  4. #4
    Join Date
    May 2007
    Location
    Thomasville, GA
    Posts
    5,998
    When I had 100A service extended to my shop, the contractor used #2 copper. What I've seen specified for 200A main service is 2/0 copper or 4/0 aluminum.
    Bill Arnold
    Citizen of Texas residing in Georgia.
    NRA Life Member and Member of Mensa
    My Weather Underground station

  5. #5
    Join Date
    Dec 2007
    Location
    Billings Missouri near Springfield Mo
    Posts
    4,552
    I had to pull my #2 alum and install 0/2 copper for a 200a service the #2 alum was only for a 60a service
    A Turn N Time
    Components for John Smith Organs and the Hobby Organ Builder

    Frog Pond Guitars


    Before you criticize someone, you should walk a mile in their shoes. That way, when you criticize them, you're a mile away and you have their shoes.

  6. #6
    There are two rules for wire sizing, one for the utility company and one for the rest of us.

    Utility companies are not bound by the National Electrical Code for the service drop to your house. Although you do have a 200amp service, you are likely to use only a portion of it at any particular time. Also, utility company with look at the transformer size feeding the houses and mountains of historical data when sizing service conductors/service sizes.

    We have a single 37.5 kVA pole mounted transformer feeding four house (including my shop that has a separate 200amp service). Considering the transformer only outputs 156 amps and it has been there for forty years, shows that the power company knows how to size the services based on real world loads and not nameplate loads. Not everything is going to be running at one time, and if you do get a spike it is for a short duration. So they don't figure your actual loads will need more than they pulled to your house. If they are wrong and the extra heating of the conductors cause the insulation to break down, then they will fix/adjust it at that time. But 99% of the time they end up being correct.

    It is not uncommon in the business/commercial world for power companies to only provide transformers/conductors at half the capacity of the rated service entrance equipment. In industrial applications where you can prove beyond a shadow of a doubt that your customer needs the full rated capacity of the service equipment, they will still only generally give you 80% of what you ask for. And again they are generally correct. Rob

  7. #7
    Join Date
    Dec 2006
    Location
    Floydada, Tx
    Posts
    1,941
    Thanks Rob. Up in NY they use 2/0 wire when they ran wire from my shop to the road. Down here in TX it seems all the companies have there own set of rules for wiring.

  8. #8
    Join Date
    Aug 2012
    Location
    Long Island, NY
    Posts
    35
    Quote Originally Posted by Bill Arnold View Post
    When I had 100A service extended to my shop, the contractor used #2 copper. What I've seen specified for 200A main service is 2/0 copper or 4/0 aluminum.
    #2 copper sounds correct. Aluminum wire has a greater resistance to current flow than copper. The specs above seem counter to that fact, #2 wire is bigger than #4, and with the added resistance - just doesn't sound right. Fortunately you got the #2 cu

  9. #9
    Join Date
    Dec 2009
    Location
    Emporia, KS
    Posts
    112
    Quote Originally Posted by Bill Nicklaus View Post
    #2 copper sounds correct. Aluminum wire has a greater resistance to current flow than copper. The specs above seem counter to that fact, #2 wire is bigger than #4, and with the added resistance - just doesn't sound right. Fortunately you got the #2 cu
    Bill,

    You missed the /0 after the numbers. 4/0 (0000) is bigger than 2/0 (00) wire.

    Ike

  10. #10
    If you have a local building code electrical inspector, call him/her and get their opinion......most of the building code inspectors I have been involved with concerning my home projects are quite amiable and will give advice freely.
    Ken
    ------



Similar Threads

  1. Tight Wire Chairs
    By Stuart Ablett in forum Flatwork Project Showcase
    Replies: 46
    Last Post: 03-02-2016, 05:12 AM
  2. Wire bender box
    By Ryan Mooney in forum Flatwork Project Showcase
    Replies: 6
    Last Post: 07-15-2015, 04:32 PM
  3. A Real High-wire Act
    By Stuart Ablett in forum Flatwork Project Showcase
    Replies: 18
    Last Post: 03-18-2015, 05:17 AM
  4. Just Under The Wire
    By Charles Hans in forum General Woodworking Q&A
    Replies: 11
    Last Post: 11-22-2014, 03:09 AM
  5. Wire size?
    By Al killian in forum Carpentry and Construction
    Replies: 5
    Last Post: 06-14-2012, 10:24 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •