OK, Ryan. If I understand correctly, I should make the 'Edison" plug referred to in the link. It is simply a plug with a wire from the neutral to the ground plug lugs. I should plug it into any one of the 20 amp outlets. And label it as a GND to Neutral bond plug.
That appears to be the recommendation. I'm only sort of happy with that for a couple of reasons:
- I'm not positive that the 120v outlet ground and neutral are 100% the same same as the ground/neutral on the 220v outlet. Please cross check that there is continuity between the 220 neutral and the 120 neutral and the same for the ground.
- I don't know the wire sizes inside the generator, are the wires for 120 outlet adequately sized for providing the neutral<->bond for the higher voltage 220 circuit? No idea.
So in general I'd be happier if the bond was actually done with some sort of bonding plate or ? inside the generator - but I have no idea how to do that.
Having said that it appears that (assuming that it does provide the bond as checked by item #1 above and of course cross checking that neutral and ground have continuity in the 220v outlet after plugging the "edison" plug in) it appears to be the "best" solution otherwise.
Second, I should make sure that my distribution panel in the trailer is grounded to the frame of the trailer.
While you are testing continuity make sure the skin of the trailer has continuity to the frame. I can't imagine how it wouldn't.. but we're here with a continuity tester and it will take less than a minute.
Third, I should make sure that the ground of the genset's 30 amp outlet is grounded to the frame of the genset.
And that is all I should do. This should properly and safely allow the genset to power the trailer's distribution panel. The other genset outlets will be marked out of service.
As I understand it yes
That said, I am unsure how to verify the floating neutral the label on the genset says the 30 amp outlet is.
You should be able to verify that with a continuity tester between the neutral and the ground plugs on the generator. If they have continuity between the two outlets then they are bonded. If they do not have continuity they are not.
Finally, my assumption is when the genset is running I should measure 120VAC between each 'hot' and neutral. I should measure 0 volts from neutral to ground. And 0 volts from hot to ground. Am I right? Before I smoke anything.
Correct except the hot->ground which will be 120v (the ground is an alternative return path if there is a short so its required to conduct the electricity). There may be some small voltage between ground and neutral (less than 2v-3v anything more is concerning; there can be potential voltage difference between any two wires of sufficient length - ask me sometime about wiring low voltage in tall buildings.. icky).
There is a nice diagram details the testing points and acceptable voltages here: http://www.noshockzone.org/rv-electrical-safety-part-iii-–-outlets/
This far a search for a locally intelligent person on this subject has been fruitless, but I am not done looking.
And the education continues.
I do wish you luck on your venture finding someone local, that would make us all a lot happier I believe!! It seems that this is a source of vast confusion even for many qualified electricians and they simply follow the rules as written without understanding any of the potential trade offs which is rather terrifying when you think about it (there are a lot of rules.. does everyone get them ALL right? what about the exceptions they sometimes matter as well).
Anyway please stay safe when testing! Glasses and rubber boots are recommended!